Convert watts to amps, amps to watts and watts to watt-hours with the official formulas, two lookup tables at 120 V and 240 V, and notes on start-up surge.
- Watts = volts x amps. Amps = watts / volts. Watt-hours = watts x hours.
- At 120 V, 1,000 W is 8.3 A. At 240 V the same load is 4.2 A.
- The US Department of Energy says the wattage on a label is the maximum draw.
- Ontario's factsheet says to use at least four times running watts for a motor's start-up. CMHC says to add about 25 per cent as a reserve.
Labels give you watts, amps or both, and a backup power plan needs the right one. The conversion is one line of arithmetic. This page gives the formulas, two lookup tables worked out in code, and the points where the simple formula stops being enough. Checked on November 24, 2026.
The formulas
Hydro-Quebec's glossary gives power in kilowatts as voltage times current in amperes, divided by 1,000. It gives energy in kilowatt-hours as power in kilowatts times hours of use. In plain terms:
- Watts = volts x amps
- Amps = watts / volts
- Watt-hours = watts x hours
- Kilowatt-hours = watt-hours / 1,000
The US Department of Energy shows the same method for a label that lists amps and not watts: multiply the current draw by the voltage. Its example is a paper shredder at 3 amps and 120 V, which is 360 W.
Which voltage to use
The Department of Energy says most appliances in the United States use 120 V, and that larger appliances such as clothes dryers and electric cooktops use 240 V. The label or manual shows the voltage and often the amps. We did not find an official Canadian page that states nominal household voltage, so rely on the appliance's own label. A plug-in power station gives 120 V from its outlets, and some larger models also give 240 V, so check the spec page if your load needs 240 V.
Watts to amps table
| Watts | Amps at 120 V | Amps at 240 V |
|---|---|---|
| 10 W | 0.1 A | 0.0 A |
| 100 W | 0.8 A | 0.4 A |
| 500 W | 4.2 A | 2.1 A |
| 1,000 W | 8.3 A | 4.2 A |
| 1,500 W | 12.5 A | 6.2 A |
| 1,800 W | 15.0 A | 7.5 A |
| 3,000 W | 25.0 A | 12.5 A |
Amps to watts table
| Amps | Watts at 120 V | Watts at 240 V |
|---|---|---|
| 1 A | 120 W | 240 W |
| 3 A | 360 W | 720 W |
| 5 A | 600 W | 1,200 W |
| 10 A | 1,200 W | 2,400 W |
| 15 A | 1,800 W | 3,600 W |
Both tables are plain arithmetic from the formulas above. The same load draws half the amps at 240 V, which is why big loads use 240 V.
Watts to watt-hours
A power station is rated in watt-hours, so convert your load. A 100 W load for 5 hours is 500 Wh. A 500 W load for 2 hours is 1,000 Wh. Our guide on calculating watt-hours walks through the full routine, including losses.
Where the simple formula stops
- Labels show the maximum. The Department of Energy says the wattage on an appliance is the maximum power it draws, so real use can be lower, depending on the setting.
- Motors start high. Ontario's farm generator factsheet says to use at least four times the operating watts for the start-up watts of a motor, and that it can range from two to twelve times in extreme cases. For heaters and lights, start-up watts equal operating watts.
- Add a reserve. Canada Mortgage and Housing Corporation says to add about 25 per cent for start-up power, and that motor starts can draw three to five times more, especially from cold.
Use the outage planner to add your loads, and see what size generator you need and what size power station you need for the next step. Typical watts for common loads are on our small appliance watts page.
Quick comparison
| Brand | Best for |
|---|---|
| EEcoFlow | Fast charging and expandable systems |
| BBLUETTI | Large lineup, expandable home systems |
| JJackery | Wide range, compact to home backup sizes |
Models with higher AC output. Check the surge rating on the spec page.
- Markets fast charging, so compare charge times
- Expandable systems in larger sizes
- Check solar input specs
Expandable options. Compare rated AC watts and Wh.
- Broad capacity range
- Expandable home-backup options
- Compare battery chemistry and stated cycle life
Range from small to large. Check the rated AC output.
- Has a Canadian storeHas a US store
- Small, mid and large models
- Compare capacity, output and warranty on the maker page
This page is general information, not electrical advice. Have a licensed electrician check any wiring.
Quick answers
How many amps is 1,500 watts?
At 120 V it is 12.5 A (1,500 / 120). At 240 V it is 6.3 A.
How many watts is 10 amps?
At 120 V, 10 A is 1,200 W (10 x 120). At 240 V it is 2,400 W.
How do I convert watts to watt-hours?
Multiply watts by hours of use. A 500 W load for 2 hours is 1,000 Wh, or 1 kWh.